Need help configuring 2 paralleled 6000xp with 2 different batteries

2 Posts
2 Users
0 Reactions
4 Views
Posts: 1
Topic starter
(@highstone)
New Member
Joined: 5 months ago

I have 2 6000xp running in parallel, sharing one EG4 indoor wall mount battery. Fully off-grid. I want to add an ECO-WORTHY 14.33kWh 48V 280AH floor standing battery to the mix. I'm thinking I would have the EG4 battery connected to the primary inverter only, and the Eco-worthy only connected to the secondary inverter (battery sharing turned off). The inverter recognizes the Eco-worthy just fine. Does anyone see a problem with this configuration? Any recommendations for other settings to change? Thank you.

1 Reply
EG4 Eric
Posts: 614
(@eg4eric)
Honorable Member
Joined: 11 months ago

No problem at all. As long as Battery Share is disabled, you shouldn’t encounter any issues. Keep in mind that the batteries will discharge at varying rates depending on the load. They will work in sync as best as possible, but it may lead to a slight difference in SOC, but as long as you monitor them and perform top balancing when needed, it will be fine.