12000xp with 3 48v V2 LL server rack batteries. Configured 3rd battery with ID 3, tried ID 4, disconnected it from bus, still went into protection mode. No clues what its crying about ....
12000xp with 3 48v V2 LL server rack batteries. Configured 3rd battery with ID 3, tried ID 4, disconnected it from bus, still went into protection mode. No clues what its crying about ....
What is the voltage on the battery that is going into protection mode?
@eric think all three were listed at 55% SOC which seems standard for the new batteries I have been getting, 51.4 or something?
Was all 3 batteries purchased at the same time? I had an issue with my setup on the last round of batteries I added where the new batteries all went into protected state as soon as i plugged them into to the closed loop coms and would only come out of protected if they were not plugged into closed loop. I had to get all batteries on the same firmware version to fix things.
@somej I did notice the two working ones were sequential serial numbers and the third was not ... they were all purchased at the same time from my local distributor