I have a pair of 6000XP inverters with a PowerPro Indoor battery. When my battery type is set for 2:Lithium, the Lithium type is 1. The EPS output that powers my house shuts off randomly for 5-10 seconds.  This may happen once a day mostly at night. I've tried other CAT5 cables, had Signature Solar check my settings, the inverter firmware is ccaa-19D0E.  There are no error messages in the logs when this happens.

I was told that I shouldn't have to upgrade the battery firmware, so I haven't yet. This never happens when I have the battery type set to Lead- Acid. Any suggestions? 

Thanks!

5 Replies
Jared
Posts: 261
Admin
(@jared)
Technical Solutions Supervisor
Joined: 1 year ago

Are any errors or warnings being reported when this is happening? My immediate thought would be EPS overload as the one Indoor Wallmount would not meet the recommended >200Ah per inverter with the 6000XP and effectively leaving you with a max of 10,240W that would be available from battery power. This would be due to the max discharge power available being 200A with one Indoor Wallmount.

Reply
Posts: 9
Topic starter
(@eshultz99)
Active Member
Joined: 12 months ago

Hi Jared, Thanks. When this happens my EPS output load is usually only 300 - 400 Watts. Sometimes lower. There are no errors listed in the Event History list.  The only thing I was able to find was in Data History. When it happens, Vact(V)= 307.3 and Veps(r)(V) = 0.   Usually the Vact(V) is 23555.3.   So, I don't know if those values are just a result of what is going on.

Thanks for the help!

I'm attaching the data file. Look at line 297 -

image

 

Reply
Jared
Posts: 261
Admin
(@jared)
Technical Solutions Supervisor
Joined: 1 year ago

It looks like the master inverter has less PV available then the secondary inverter. I would recommend making the inverter with two arrays as the master inverter to see if this corrects the issue.

Reply
Posts: 9
Topic starter
(@eshultz99)
Active Member
Joined: 12 months ago

I will make the change and report back!