Woah! The latest firmware (released today!) Seems possibly to have fixed the problem!Not a single EPS overload today!
I have this inverter. It does not “trip the breakers”, the 200A battery breaker is not electrically controlled. It does shut down the inverter (all ou...
I have more data. I experimented today with turning off the solar disconnect and it instantly solved the problem. The 6000xp had been ramping down the...
@eric Yes, now that I have a BMS, it does a better job of getting the voltage. I've also ramped my max amps up to 200A (charge and discharge). And yet...
If EG4 is working on this problem, I'd love some statement that says so and I'll wait for the next firmware. If more data is needed, I'm happy to give...
Strangely enough, the "BMS Event" Column shows 0x6659 which is 26201 in decimal, the same as all those other corrupt fields.I don't even know what "BM...
I'm seeing this again... notice that the max charge / discharge amps are always being sent as 90A. It appears like the inverter gets one bad packet (f...
For what it's worth, and you're likely aware, but there's a *whole* bunch of people with this problem in the diysolar forum:br />
Also, a related side-question: Does the 6000XP care about and interpret the cell voltage and cell temp values from the pylontech RS485 protocol? IT pa...
I've been following a protocol spec from Pylontech (RS485 pylon version 3.2). Is this the spec that the 6000XP implements for Lithium Type: 2 ? OR is ...