I am planning to wire in a 10kw westinghouse to an off-grid 12000xp today. I do not have the westinghouse "smartswitch" delivered yet, so I can't use ...
@eg4eric great, thanks. If I want to test and manually fire up to generator before the voltage drops to 50v.... what is the best way to force the i...
@eg4eric yes, the current open loop LFP charging is a bit of a kludge. I'd be happy to work with the team to define the desired behavior, and/or beta ...
@eg4eric , the charge curve and behavior we really want to see for open loop charge control of Lithium batteries is a simple CC-CV curve where:- daily...
Just wrapping up this thread with a recommendation... When installing and powering up a new Inverter with a battery you *should* use a pre-charge re...
@eg4eric thanks Eric, I do have another major issue/question/bug that probably needs to get to Engineering and handled as a firmware update. I started...
@eg4eric thanks, I am in contact with Callie in CustomerOutreach.... I think making progress.
@eg4eric The Seller (offgridsource.com) is giving me a total runaround. First requesting videos, then still photos, then the serial number, and then ...
@krzysiek_kta it is not great for LFP to hold at 56v, and its hard on the BMS and charge controller to cycle on and off. There needs to be a reasonabl...
@krzysiek_kta I don't want closed loop comms, I want to program voltage setpoints. This is working correctly finally on a 6000xp system that is offgri...
I had the same problem with the first 6000xp I installed.... and it was eventually resolved with a firmware update. I would have hoped the same logic ...
@eg4eric 6x Midnite Solar powerflo-5. I do NOT want to use closed loop comm cables, which is why I set parameters as shown in top post to enable the ...
Here is a picture.... voltage is floating at 56 instead of 54 as defined. I consider this to be a BUG, and not happy about it since holding batteries ...