Was all 3 batteries purchased at the same time? I had an issue with my setup on the last round of batteries I added where the new batteries all went ...
Same issue with the 18K and the 6000XP: @pawnee posted a video of his "brownout" as well here:
Typically, yes, the less power you use from the generator, the less the THD the generator outputs.
I needed 200amp pass thru because of peak draw in summer also so I bought 2 12000xp's. It wasn't that much added cost if you use Polaris connectors. 1...
How about if I used the Grid boss with a 12K Sol-Ark all in one hybrid converter? Would the Solar Edge inverter still be needed? Normally I would pa...
I believe you already have a Victron smart shunt on your system connected to the Cerbo. With FLA batteries, that's already the best solution you have ...
Thought I’d post a short video of the brownout that I’m still fighting.
@brokenpointjoe it should have worked at those low amps. And FYI on the 18k screen on the generator charge it says Amps but it’s Amps dc. I had my ...
@ron My generator like most does produce dirty power. I use Line and Load reactors on 30-40 VFD’s here the farm. I’ve been thinking about putting ...
You cannot share an array between multiple inverters/mppts. They will end up fighting with each other trying to find the maximum power point. You ca...
You cannot use the Cerbo GX to monitor the 18kPV. Without battery communication to the inverter, everything will have to be based on voltage.
The gridboss is not an inverter, it's basically an interconnection device between inverters, the grid and loads. You should be able to AC Couple t...
The panels are rooftop and the inverter is on an exterior wall on my house in MA.