no luck using logic or any other method. It opens communication with bmstest, but does not identify any addresses. I know on some batteries the dipswi...
Yes. My Chargeverter keeps its settings for charge current, etc. and I keep it powered down - no AC or DC connections. <EDIT> I just re-chec...
@dougl Thank you. That makes sense. I will hook up the application software again and re-check. I will say we've done this and I sent the data (scre...
@ldfly If you have access to the BMS to look at the cell voltages or even just the Max Cell and Min Cell voltages look to see what the voltage diff...
Yes - it's working better. Signature set the "stop charging" from 56 -> 55.4. I would never reach 56V when charging. That seemed to get the Inver...
The battery cells on all 3 batteries are now showing ~40mV difference at the high charge voltage and I also notice the charging profile now includes d...
Hi @brdfrd , I'm just curious if you ever got your generator automation set up. Hopefully you found some voltage settings which got this system work...
Do you have a PV string(s) connected to that inverter? If so, use your disconnect and remove that string(s) from the inverter. Clear the error and s...
As stated above bulk at 58.8v float at 58v would cause stop start cycling.. Currently I have it set to bulk at 58v and float at 57.5v. Thanks, ...