Yes, this is still happening, but now there is a new issue. I have lost all communications with the inverter. I cannot even select a system name becau...
@eg4eric Obviously the battery voltage varies over the course of a day. Attached is the graph showing the battery voltage for that day. The cut-off ...
@jckemp3 Curious. I don't have that menu. I wonder if there has been a system upgrade that I don't have.
@jckemp3 I haven't restarted the inverter yet, but I will. The system is continuing to behave as if there are no batteries. The inverter is an 18kPV. ...
@jlankford Thanks for the suggestion. Actually, I did not even realize the indoor batteries had heaters. I thought only the outdoor version had them. ...
And another mystery. At 5 am when there is no PV activity and no battery discharge, I export power to the grid for 5 minutes.
@jlankford These are the INDOOR wall mount batteries. Per the manual, the heaters will come on at 32 F and turn off at 41 F. My basement temps might g...
@jlankford Here are the graphs for 2/1/26 and 2/2/26. What do you surmise, or what would you expect to see?
And it is still happening - day 2. Am I powering the universe? I do not know if it is significant, but when I "READ" this, it always times out. So...
I had the same issue, but it begs the question: Why would you NOT set the battery type to EG4 rather than "1"? They are EG4 batteries. I have wasted a...
How do I send a private message?