Tools like Footprint Hero can also be helpful, though they may be somewhat generic. Footprint Hero Solar Panel Tilt Angle Calculator
As Adam De Lay mentioned, our hybrid inverters are designed to connect to the GridBoss Hybrid Ports using the AC IN port, enabling bi-directional powe...
When connected to the grid, the loads will switch to grid power if PV power is unavailable, and the battery reaches the on-grid EOD. To enable AC char...
It looks like the master inverter has less PV available then the secondary inverter. I would recommend making the inverter with two arrays as the mast...
The first inverter powered on will take the role of "master" inverter. However, if these are paralleled on the monitoring system, I would verify the s...
I would recommend setting the discharge current to 350A with the two Wallmounts paralleled to the three 6000XPs.
Are any errors or warnings being reported when this is happening? My immediate thought would be EPS overload as the one Indoor Wallmount would not mee...
The generator input can be adjusted using Setting 18 on the LCD display, and GEN boost can be enabled or disabled via Setting 30. Regarding ...
You will have the 120/240v output with only battery power available.
Here is the recommended lithium brand and the pinout configuration for the BMS port on the inverter for RS485 and CAN communication: Lithium Brand O...
With the 6000XP having an IP20 rating, I would not recommend having it outside. I would also take in consideration the operation temperature range of ...
Is this for the 6000XP or the 6000EX? I’d also recommend having only one neutral-to-ground bond in the system. This bond is usually located at the fir...