Feel free to send me a DM and I can help get this corrected.
The account has been disabled, and the post have been removed.
@brdfrd you would only need to charge the battery bank in lead-acid mode once, until it triggers the battery overprotection warning once one cell hits...
Could you post the firmware version from the LCD display? Also, on setting 3, is the GNE setting available?
I would make sure that the AC Charge is enabled with the Start AC Charge SOC and Stop AC Charge SOC configured.
The Dry1 dry contact ports are currently the only option for wiring a 2-wire stop/start with the GridBOSS. Dry2 is unused at the moment and reserved f...
It really depends on the generator's THD rating. It might be beneficial to enable GEN Boost and operate the generator at around 50-70% capacity to ens...
@brdfrd I prefer lead-acid mode for this.
That’s mostly correct. However, you might find this link to our API documentation for monitoring helpful: https://eg4electronics.com/api-documentation...
I will check to see if there is an update to this report.
Without looking at the system I would reference page 30 of the manual that talks about the return points for switching back to battery power. How...
If the generator's total harmonic distortion exceeds 5%, there’s a risk of damaging sensitive electronics and failing to charge the batteries using ge...
@brdfrd I would set charging to based on voltage to make sure that the cells reach the overcharged warning protection.
The minimum amount of discharge amperage reported is 0.5 amps DC.
@brdfrd the dip switch order is correct. Would you be able to charge the battery bank up to roughly 57.4v or until a cell hits 3.6v on each battery an...