RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@jlankford On the 6000 the "AC Charge Enable" is not an option. I am assuming that since there is no sell back that the option is always on. (just an...

9 months ago
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@joel-brodeur On the 18Kpv, there is a setting "AC Charge Enable" which I do not see in the above screen shots. Is that not a setting applicable to...

9 months ago
Reply
RE: Another Generator question

@pawnee Glad the update fixed the Gen run, did it also fix the Watt readings? Hopefully @eric has some news or suggestions on the hard handover. J...

9 months ago
Forum
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@mylesj I am guessing you can't disable it. Maybe just set your gen start SOC to something like 20%. Also, if you haven't already, you might try, r...

9 months ago
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@joel-brodeur Hello Joel, I tried you suggestions and it did not work. I have tried to disable the generator setting and it wont allow me to do it...

9 months ago
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@joel-brodeur Hello Joel, I tried you suggestions and it did not work. I have tried to disable the generator setting and it wont allow me to do i...

9 months ago
Reply
RE: Another Generator question

So getting the firmware completely pushed through got my generator running like it was before, but I’m still getting a browout/hard handover. Bad enou...

9 months ago
Forum
Reply
9 months ago
Topic
Forum
Replies: 2
Views: 1025
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@mylesj I notice that you have the Gen settings also set. Are you using a gen to charge as well? If not you might try disabling the gen charge setti...

9 months ago
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

@joel-brodeur Thank you Joel! I just tried your suggestion. Still nothing. I hit the quick charge button again and it says its charging but it is n...

9 months ago
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

From the "E G 4 ® 6 0 0 0 X P M O N I T O R S Y S T E M W O R K I N G M O D E S" on page 4. EG4®-6000XP-Monitoring-System-Working-Modes.pdf

9 months ago
Reply
RE: 6000XP no solar, used as backup generator only, AC Charge will not work

Have you tried setting you AC charge times to - 00:00 to 23:59 JB

9 months ago
Reply
RE: Gridboss not reporting and showing offline

@eric any update on this. I am seeing a similar issue after bringing the nging my Gridboss and Flexboss21 online last night. The Gridboss does not sho...

9 months ago