I would make sure that the AC Charge is enabled with the Start AC Charge SOC and Stop AC Charge SOC configured.
@joel-brodeur I would hope that's not the case. Seems like the software engineers made a mistake if it is. Sounds like this would need a test with...
@jared thank you so much for reply! So, to recap: the wire #23 (+12 VDC) goes to NO1 the wire #194 (Transfer) goes to COM1 the wire #0 (DC Commo...
@jlankford @jared Additional thinking: If the above is true, then I think this would imply that the gen is getting a shutdown signal prior t...
The Dry1 dry contact ports are currently the only option for wiring a 2-wire stop/start with the GridBOSS. Dry2 is unused at the moment and reserved f...
I wonder if the problem isn't the switching speed but the range in which the switching occurs? Assumptions based on mentoring center (and a healthy ...
@ron According to this document - G4-254 - it looks like all they say is "Total harmonic distortion (THD) from no load to full load with a linear load...
For reference, here's the generac wiring diagram:
Only thing I could find quickly online for 12RESVL High Quality Power. Kohler generators provide advanced voltage and frequency regulation along...
Thanks Jared, This is useful From what I can tell, this api supports http get and post requests to /p> And the requests are authenticated (presu...
It really depends on the generator's THD rating. It might be beneficial to enable GEN Boost and operate the generator at around 50-70% capacity to ens...
@jlankford Thank you for the clarification. That makes sense. JB
I see the inverter limits the wattage to 90% of what you enter, but I'm not sure how that all works with 2 inverters. The 12RESVL Rated kW LP 12 kW ...