RE: BONDING SCREW

Is this for the 6000XP or the 6000EX? I’d also recommend having only one neutral-to-ground bond in the system. This bond is usually located at the fir...

2 years ago
Forum
Reply
RE: EG4 website - Missing Battery Detail Data

Would you be able to DM me the serial number for the inverter? I would like to take a look.

2 years ago
Reply
RE: Eg4 18kpv dongle without wifi

I recommend this guide, even though it's listed for the BJxxxx, BGxxxx, and BExxxx dongles—it should still be useful: EG4 Wifi Dongle Troubleshooting ...

2 years ago
Forum
Reply
RE: North Central Texas Setup Just about to turn a year old!

They have arrived! {emojis}:grin: A bit delayed by NM Snowstorm. . . Thank You. RPS & FedEx! The new posts have been set b...

2 years ago
Topic
2 years ago
Forum
Replies: 5
Views: 2043
Topic
Forum
Replies: 2
Views: 1047
Reply
RE: Error 28 on 6000XP quite often

I am learning a little as I go. When I check the maintenance setting for battery discharge current it shows 140, EXCEPT when I click READ, then it ind...

2 years ago
Reply
2 years ago
Forum
Reply
RE: Battery imbalance

@jared the V1’s are the newest firmware. The V2’s were bought last month. I’m assuming the latest it I can try loading the BMS test for them and make ...

2 years ago
Forum
Reply
RE: 6000xp load side voltage

Yes, I found the issue. The neutral wire wasn't connected to the bus.

2 years ago
Forum
Reply
RE: 6000xp load side voltage

Just out of curiosity, and I am sure you checked but, when you are checking voltage from L1 and L2 to Neutral, are you reading Vac or Vdc? The reaso...

2 years ago
Forum
Reply
RE: 6000xp load side voltage

Are there any other AC inputs? If so, it will be in bypass mode and mimick its power profile. For example, I've seen 50-60v when using a 120V generato...

2 years ago
Forum
Reply
RE: EG4 website - Missing Battery Detail Data

Thank you. I set the RS484 protocol of battery #1 to P02. The inverter and battery #1 BMS were power cycled. But - still no details of the 4 batter...

2 years ago
Reply
RE: 6000 XP set solar charge limit?

@jpangburn, Agreed. It would be nice to know. My guess is that the first battery is the one that is used. As far as I can tell, the batteries don'...

2 years ago
Forum
Reply
RE: Wall Mount Indoor Batteries 100% @ 53.3 Volts while charging with Chargeverter

I recommend continuing to charge with the Chargeverter up to 56.2V. Although the BMS won’t trigger overvoltage protection until a cell reaches 3.8V, 5...

2 years ago