I bet it’s your charge amp setting. What is it set at? If I remember right that setting is in DC amps but it doesn’t say that. It’s been a while but I...
What settings do you have configured for the Generator Charge?
The Chargeverter will definitely help with the charging and cleaning up the dirty power. Thank you for updating us!
I know we are working on a new EG4 Monitoring app but don't have a release date yet. I noticed that your Lithium Type is set to 6. For Lifepower4-V2 b...
Thanks for this. Will the inverter be able to auto-start the generator using the 2 wire start in this configuration? And in case it's pertinent, w...
Okay. I get way more information on the desktop site. It looks like while the voltages are all very close the SOC is widely different between the batt...
Make sure you have the Discharge current set to 280A. This has to be manually changed or else the battery discharge will be set to 140A which is what ...
Eric, it switched back over off the grid. but, the issue is with the mobile app, it does not correctly set the AC charge parameters. I was able to get...
What is your inverter's serial number or station name? I can take a look at it for you. For the Batteries SOC, you can Top balance them. Charging them...
The batteries reappeared and it's at 25 percent now, but I don't know how to get it to stop using grid bypass. I have it set to only do grid bypass at...
I'm looking for the wire size the terminal can accommodate. I know the recommended is 8 AWG. And you've seen 6 AWG. But, what is the maximum size?
Hi Gang! Thanks for all your comments. I had technicians out to look at it and spoke with several eg4 reps and seems the power is too dirty, they'll i...