EG4 Community Forum

12000XP max wire si...
 
Notifications
Clear all

Question 12000XP max wire size

5 Posts
4 Users
1 Reactions
1,875 Views
Posts: 9
Topic starter
(@sunnyside)
Active Member
Joined: 1 year ago

Would it be possible to update the 12000XP manual with both the min AND max wire size for AC wiring?. So both min and max are clearly documented? Along with recommendations for AL vs. CU. It seems possible since that is the way you have it in the 18kPV manual.

Reference: 12000XP manual (10/31/24 edition)

 

18kPV
12000XP

 


4 Replies
Jared
Posts: 261
Admin
(@jared)
Technical Solutions Supervisor
Joined: 1 year ago

I will forward this request to our technical writing team.


Reply
Posts: 22
 ray
(@ray)
Eminent Member
Joined: 1 year ago

Is there an answer to this though? Also, should we be using lugs to connect, or bare copper? If lugs, what is max/min sizing. 


Reply
Posts: 12
(@solar_pergola)
Active Member
Joined: 1 year ago

So what is the answer? The manual strangely still lists the minimum wire size...

 

I'm assuming 1/0 aluminum will fit the load and grid holes?

 

What about the N?


Reply
Posts: 12
(@solar_pergola)
Active Member
Joined: 1 year ago

Hi Solar Pergola thanks for reaching out. 

The load breaker will accommodate up to 1/0. And the grid terminals will also and N busbar. Although the ground bus bar won't take 2awg. 

- Not the EG4 Support team


Reply
Share: