Hello, my apology is this was covered already, just not having good luck finding exactly the same situation.

We have a 6000xp that we want to run in UPS mode, a long with 100ah eg4 48v battery. No solar, just grid power + battery.

 

It does work, but it's also continually charging and discharging the battery, non stop. And during some of the switching the light and some of the power supplies flicker or cycle. 

 

I have two questions:

1. Is it possible to set up inverter to use grid power always until power outage?

2. We have 120/208, is there some setting that controls the 208 vs 240? Or is that automatic?

 

Thanks

 

3 Replies
EG4 Eric
Posts: 517
(@eg4eric)
Honorable Member
Joined: 9 months ago

It should automatically detect it; however you can manually set it to 120/208 through the application settings on the Monitoring website, or you can use setting #4 on the inverter screen to set it.

You can set the AC First start time from 00:01 to 23:59 to allow AC power to run the loads all day and preserve the battery. Keep in mind this is an off-grid inverter, so it primarily relies on battery and solar, but using the grid to power the loads throughout the day is possible.

image
Reply
Posts: 1
(@golfleep)
New Member
Joined: 2 weeks ago

I'm trying to accomplish the same thing (6000xp + battery, fucnting as UPS, no PV connected) but struggling with the settings. If I place the inverter in AC charge mode, the inverter continuously cycles between charging and discharging the battery. If I place the inverter in AC first mode as suggested above, the battery does not charge at all even after grid power comes back up after an outage. Is there a setting to have charging occur in AC first mode (but with no PV connected)?

Reply
EG4 Eric
Posts: 517
(@eg4eric)
Honorable Member
Joined: 9 months ago

When you set AC Charge, set it based off SOC, so this way the inverter will charge batteries with grid when the batteries go under a certain battery percentage, and you can still have AC first configured to power loads. This configuration is a little difficult to achieve as the 6000XP is an off-grid inverter, which primarily relies on battery and PV to power loads.