Hello everyone,
I'm looking for assistance from EG4 technical support and other EG4 6000XP owners who may have experienced similar problems.
I have three EG4 6000XP inverters operating in parallel. My middle inverter has been experiencing recurring Fault 17 (Internal Communication Fault 2), along with complete loss of PV production.
Symptoms:
- Fault 17 appears intermittently, sometimes remaining active.
- Both MPPT inputs stop producing solar power.
- PV production drops to 0W, even when the other two inverters are generating normally.
- The inverter previously made abnormal popping sounds associated with the PV side.
- With PV disconnected, the inverter sometimes displays approximately 12V on PV1 and PV2.
- Fault 17 eventually disappears when the inverter enters standby, but the underlying problem remains unresolved.
Firmware history:
Signature Solar remotely updated the affected inverter on September 30, 2026. The other two inverters received firmware updates on October 2. All three currently report firmware version ccaa-1E1515.
Unfortunately, on October 9, Fault 17 returned on the same middle inverter, and it was producing absolutely no solar power.
I have currently isolated its PV input, GRID input, and AC output as a precaution. The inverter remains battery-powered for monitoring.
Similar case found on this forum:
EG4-6000XP – MPPT1 ghost voltage + both MPPTs get stuck after clouds
This customer's symptoms appear remarkably similar to mine, including Fault 17, unexpected PV voltage readings, and MPPT production failures. I noticed that EG4 Eric suggested the inverter might require replacement. The thread does not confirm the final repair or replacement outcome.
My questions:
- Has EG4 identified a known hardware failure involving the 6000XP MPPT board or its internal communication circuitry?
- Can Fault 17 return even after a successful firmware update?
- Does the MPPT firmware require PV power during installation? My original update was performed with PV disconnected.
- Is approximately 12V displayed on disconnected PV inputs normal, or could it indicate an internal MPPT problem?
- Has anyone experienced these exact symptoms and successfully resolved them?
- Given the recurring Fault 17 and previous popping noises, would EG4 recommend replacing the inverter rather than attempting further firmware updates?
I have photographs, screenshots, and previous technical-support correspondence available.
I would particularly appreciate assistance from @eg4eric or another EG4 technical-support representative.
Thank you!
Supporting photos and app screenshots:
The app screenshots below were captured after isolation of the affected inverter; the LCD photo shows its later standby condition.
LCD in standby: 12V PV reading and warning 26; this is not a photo of Fault 17.

PV disconnect switch.

Affected middle inverter app screenshot: standby, 0W PV and firmware ccaa-1E1515.

Other inverter: 3874W PV and the same firmware.

Other inverter: 3038W PV and the same firmware.