Apologies - this is a repost because I'm not sure anyone was seeing the original. Thanks for your patience.

I'd like at least something from the EG4 tech staff that says they don't release any info about the protocol.

__________________________

Greetings:

TL/DR: How to fix comms failure between FlexBoss/Gridboss pair that are 270ft apart.

            RS485 signal booster being considered - recommendations?

Details:
Our off-grid community recently (Oct) installed a FlexBoss/Gridboss combination that are separated by about 270ft (buried cable length).

The original installation was working but after replacing (under warrantee) a miss-behaving Flexboss we have a persistant "W030: Grid Boss CAN Loss" error.

Would something like a: <a href=" removed link " target="_blank" rel="noopener">RS485 Extender   work to boost the signal?

_________________________________________________________-

Misc Info:

Yes, I've used a circuit tracer to check the continuity of the cable. It's a high quality, certified for burial, cable. 
Yes, I can/will re-do the connectors and try to shorten the cable (might get 3ft...), but a better, more reliable solution would be to strengthen the signal.
Yes, we could lay fibre (not clear that would work), but I don't want to dig up our road again if we can avoid that in any way.

Why this setup?

  • The original manual specified a 300' limit and we knew we were within that. Later versions dropped it to 270' so we shortened the cable as much as we could to get it working the first time.
  • The Gridboss sits in our generator/power shed where we want to use the Smartports to control our septic system pumps and run them off batteries rather than the generator. The Flexboss sits in a separate community building with 21kW of solar panels.

3 Replies
Posts: 1
(@oksolar)
New Member
Joined: 5 months ago

Hello Zirrad,

 

Did you have any luck with this issue? I am currently going through a similar issue and am struggling to find a solution.

 


Reply
Posts: 4
Topic starter
(@zirrad)
Active Member
Joined: 9 months ago

Not yet - but have some info:

EG4 is re-skinned LUXPower electronics from China - the ports run CANbus and someone has reported successfully using a CANbus repeater:  A GCAN-226 

image

Literally today, the one I ordered from China arrived today - I'll be able to try it next week.


Reply
Posts: 4
Topic starter
(@zirrad)
Active Member
Joined: 9 months ago

Discovered that the 120Ohm dip switches for the parallel ports were not switched on.

Not mentioned in any of the calls with EG4 tech people.

Only figured this out after steeping myself in CANbus protocols and having the right glasses on when I went to install a booster - and yes it's also in the manuals so I am embarrassed. 


Reply