@jpangburn ... not pointless to be concerned, but better to be educated. using LFP in cars is far different than solar; mostly because of the charge c...
@jpangburn if you are running with closed-loop rj485, and have successful communication, then setting battery type to Li (lifepower4) lets the batteri...
@jared , you gave an incorrect and incomplete response.... a. LFP charge curve *should* bulk charge to 56.2, and float at 53.5-54.0 for best results...
@jarrett , I'd be happy to be a beta-site tester at one of my client sites if there is a patch available that can be installed with the remote update ...
running off-grid, you really do want to charge to 100% every day possible to start the night with full batteries. A 'correct' charge curve for LFP bat...
Still, no response or followup ? very disappointed in EG4 at this point. I'm going to have to evaluate other inverters, or add external charge control...
@jarrett .... kinda expecting an update by now. It's pretty serious to not be able to set correct bulk/float voltages. I would hope that the 6000xp ch...
@jarrett , yes we had emailed back and forth several times.... This new forum will be a decent way to track open bugs, and let people know when patch ...