Yes, 100% should be around 56.2V. You can temporarily switch the inverter to Lead Acid mode and set the Charge Voltage to 56.2V, the Float voltage to ...
@thomaspugmail-com After further investigation, I was able to find that you should be able to update the LCD remotely through the monitoring website a...
@simply-efficient If you have one or more inverters connected in parallel, make sure they are all set to standby. If you’d like, you can send me the s...
@thomaspugmail-com The LCD V18 will fix this issue. EG4® 12kPV All-In-One Hybrid Inverter - EG4 Electronics
This issue may be caused by a loose connection. I recommend double-checking all battery cables to ensure none are loose. Have you also tested the batt...
Make sure that you have a specific network for 2.4GHz and don't have any special characters in the Wi-Fi password.
That should be correct for the 12kPV. You shouldn't have any issues. However, If you run into any issues with the inverter, feel free to reach out. We...
Hello @tlane17, exactly what you need help with? I’ll do my best to assist you!
@ron I'm sorry, could you provide more detail on what you're referring to?
Is your system producing enough solar to power loads and charge batteries?For the Battery Priority Start Time 1, try setting to 00:01. If this still d...
You can use the app or the monitoring website (Maintenance Tab) to update your inverter to the most recent firmware. Version 20 of the LCD firmware is...
Is it showing any warning or Fault codes on the screen or is the screen staying the same as the screenshot then just turns off?
@chris07x The Power Backup feature controls the seamless transition of the inverter to battery power when the grid fails or is interrupted. Enab...
We are still conducting internal testing. Version 0405 remains the current standard release.
@eareyes20 Can you share your inverter's serial number or station name so we can look into this issue for you?