Thank you for bringing this to our attention, and we apologize for any confusion regarding the Daylight Savings Time feature. The DST feature was de...
@jxnhrprAre you able to share some pictures of the connections on the batteries at the inverter and on the batteries? I can begin to make a ticket and...
@bobcThe Flexboss21 does have Mechanical Terminals
@jxnhrprThe batteries need to be set to ID 1 and ID2 and have the BMS reset. Just pushing the power button off then back on. Are you getting voltage o...
@anothereg4userGood afternoon! 1. Is periodic re-balancing/re-calibration necessary or recommended for my system/configuration?We recommend an 80% D...
@heshy Thank you for your input! I agree with you, and I will be sharing this with our team. If necessary, I can also install the beta firmware on you...
@solar2025If you have the Ct's located between the meter and the main panel, you will be getting the readings of any power coming and going to the gri...
@wildbillpdx If you are trying to get a 280ah WallMount battery, a Lifepower4-V2 and a Lifepower4-V1 you shouldn't need the multipack firmware. Just m...
@bobandroslynFor the 18kPV the lowest that it can be set to is 140v.
@tsuga Thank you for sharing!
I can help you resolve this issue. Could you please provide a picture of the 18kPV so we can confirm the unit?
@gtsquires I don't believe I made any changes to your system.PV Charge Priority limits PV charge power. So, if you set it to 3kW, it will only use 3kW...
@okiesolie Great! Please let me know if there is anything else anything else I can assist you with.