Yes, I did also mention the switching to generator. However, I believe most reports have been when switching back to battery. As soon as I hear the fi...
Thank you. I have seen this video and it is a different use case. He appears to have his inverters output set for split phase to a 240VAC double pole ...
Yes, here you go.But, regardless of settings, I thought the 6000XP should stay in bypass mode for 4-5 minutes before attempting to exit (for W28 error...
Were you able to get this issue resolved?The firmware update should have fixed the issue.
@eric The batteries did reach 100%, but the arrow direction shows from inverter to battery and 90W going into battery while forbidden is set.
Typically, when the batteries reach 100%, you will see "BMS Charge Forbidden," indicating that the battery is no longer accepting a charge. Do you rec...
Can you post a screenshot of where you are seeing this setting?
The GridBoss is only compatible with hybrid inverters, such as the FlexBoss and the 18kPV. The 12000XP and 6000XP are off-grid inverters and are not s...
Unfortunately, this is not possible at this time. However, I will submit a request for consideration to lower the charging voltage in a future firmwar...
Are you able to post screenshots of your settings please?
I believe this is saying you can do up to 60A for 2 inverters, 90A for 3 inverter and so on. I attached a link where someone explains how they install...
Charging and discharging by voltage for a long period of time shouldn't be an issue. When you installed the new V2 batteries, were they within 0.5V of...
@eric Thank you, Eric. No worry at all! I'm considering an alternative setup: integrating a 6000XP (or possibly a 3000EHV-48) inverter to connect the ...