Have you tried disconnecting the generator to see if the warning stops showing up?
If you send me your inverter's serial number, I can help you with the settings.If you can, also share some pictures of how you have the generator conn...
@eg4eric Any progress?
Ive got a 6000XP installed around one year ago. We have a 240v Generator which we want to use to top off batteries on occasion. Currently, it only bri...
I actually just realized where my symptoms are coming from: The 140-160W I was getting last week was from having the EPS enabled. I've disabled it ...
@eg4eric Thanks for checking, Eric. The problem (failure to 'enable battery backup mode') still persists. Even worse, I cannot discharge the bat...
Reading the literature, it seems that by only using the grid during a PV Charge Priority window, and not allowing off grid mode to go from Grid Use ba...
I don't know what picture of the inverter you want? Physical connections of solar or pictures of the display? PV Input settings - Home display....
@cfrancisco Can you please share your inverter's serial number?Were you wanting all the data cleared?
@old76ta Try setting the Lithium Type to 1. If it's not working on 1, then we can check the cable and connection between battery and inverter. Lithium...
@fkitzmannCan you post a picture of the inverter? if you can a picture of the whole system, so I can get with my manager on this issue.