[Closed] EG4_ccaa-190D0E

1 Posts
1 Users
1 Reactions
628 Views
Jared
(@jared)
Posts: 252
Online Support Admin
Topic starter
 
2024-08-26
  • Based on standard firmware ccaa-180C0D.
  • 1.Add Smart load function.
  • 2.Add AC couple function.
  • 3.Add 127/220V three-phase option for EPS Voltage.
  • 4.Add 120V grid charge function. (it can only be connected to L1-N 120V grid and load)
  • 5.Add phase sequence adaptive function for three-phase parallel operation.
  • 6.Optimize the AC input/output reverse connection detection function
  • 7.Optimize the BUS voltage high issue when the battery is fully charged
  • 8.Optimize AFCI detection
  • 9.Optimize N-PE detection
  • 10.Optimize BUS balance adjustment function
  • 11.Optimize internal communication fault issue due to high grid or generator frequencies
  • 12.Fixed occasional output shutdown issues in the parallel system after power outage and go to off-grid mode
  • 13.Fix the issue of charge current exceeding the limit when connect to AC charge in PV charge mode and the parallel system.
  • 14.Fix the issue of comm address not being re-assigned when re-plug and unplug the parallel comm cable.
  • 15.Adjust the upper limit of the mains frequency to 65Hz. The phase-locked frequency of the generator is 65Hz, and the upper limit of the frequency is 67Hz. Prevent the generator frequency from triggering protection during normal frequency fluctuations.
  • 16.Improve the rated power of the 100/200V EPS voltage mode to 5500W.

     

 