EG4 Community Forum

Odd 12000xp behavio...
 
Notifications
Clear all

Odd 12000xp behavior when coming off grid-charge to Solar/Battery mode.

29 Posts
3 Users
3 Reactions
5,818 Views
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

Latest firmware on all batteries. ceaa-0507 on 12000xp

- I have 2 12000xp in parallel and 6 eg4 wallmount indoor batteries. 

- They are operating in communication mode for state of charge.

- i have it set to charge from 20% to 60% SOC @10amp for each inverter.

SOMETIMES, not all the time, BUT SOMETIMES when finishing the AC charge cycle ( i have it set to stop charging at 60% SOC), it will swap over to PV Off-Grid mode (basically wont charge my batteries) rather than the PV+BAT Off-Grid mode. I am able to force it out of PV-Off-grid mode by hitting the "start quick charge" button in the app

This is easier to visualize with the solar assistant chart. 

image

The end result is that I have to sit here and babysit this thing or i lose out on a bunch of PV power! please help!



   
Quote
Topic Tags
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  
image

I do notice that the Batt Status goes to "2". unsure of why the batteries are affected by it swapping over.



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

On second look, This appears to be a battery communication issue. Any ideas as to what is causing that? It appears to happen when PV is really charging big time. 

I wonder if interference or something on the CAN ethernet wires? anyone had that happen before?



   
ReplyQuote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 2 years ago
Posts: 1287
 

Which Lithium Brand do you have set on the inverters?

Make sure you have 1, as this is the best communication protocol to use with the WallMount batteries.



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

The inverters are set to LITHIUM 0 (these are 12000xps, there isnt an option for eg4)

The batteries are set to EG4/Lux

@eg4eric I checked every battery. they are all dipswitched correctly 1 through 6. 

They are all on the latest, correct firmwares (thank yall for sending the required cables to update!)

image

Again, 99.9% of the time, the communication is perfect. Sometimes it drops out and it seems to happen when the solar energy is really pumping.



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

@eg4eric

 

Wait... I had it set to Option 0 for standard.

 

But you are saying it should be set to Option 1 HinaESS? Why is it not called EG4? Lol.

 

I'll leave it at option 1and see if If that has fixed it... Thanks.

 

PXL 20251211 031354591


   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

Ok new weird stuff happened today:

image

At 1038 it goes into pv batt/ac charge mode without any input from me.

Then at 11:03 it goes into that same PV Off-Grid mode. 

it only recovered because I cycled both units.

---------------------------------------------------------------

I did notice that the battery communication cable was connected to the slave, so possibly that has something to do with it? Going to continue to monitor. really would like to see some logs on this. It should log and say why it's changing operating states! 

If anyone has ideas, let me know.



   
ReplyQuote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 2 years ago
Posts: 1287
 

@clarktheshark Yes, 1 is correct. That is the correct protocol. Also, having the master battery communicate with the slave inverter can definitely cause issues. I recommend updating the firmware on all the batteries. Both the RS485 and also the RS232.

EG4® WallMount Indoor 280Ah Lithium Battery - EG4 Electronics

image

 



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

Check: Batteries have latest firmware for both rs232 and rs485. 

No issues since I swapped the battery comms from the slave inverter to the master inverter. (4 days trouble free).



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  
image

Well, it happened today. battery charging stopped for 10 minutes almost exactly at 11am. This time it recovered by itself without any intervention. what could be causing this?

@eg4eric



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  
image

The only thing i notice thats different on the data logging is that the BATSTAT goes to 2 vs 3 when it goes into these ~10 minute periods of not working. (always during high solar output)

I cant find any documentation on what that means.



   
ReplyQuote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 2 years ago
Posts: 1287
 

@clarktheshark

Are all the batteries updated with the latest firmware? You can check by using BMS Tools Software

We don't have any documentation on that; however, we have had this issue before and updating the firmware on all the batteries to the latest firmware resolved the issue. 

Can you possibly share pictures on how the batteries are connected and how the Master battery is connected to the Master inverter?



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

I had installed the latest, the issue still persisted. 

Reminder that i had 4 batteries, then added 2 more ~6months after the initial install. 

This is today. The charging always drops for exactly 10 minutes in the peak of the day. sometimes several times a day.

image

The install is fairly normal i would say:

image

 

image

- batteries are configured 1 through 6 from left to right. 
- master 12000xp inverter happens to be on the right.
- I have a transfer switch configured to allow me to bypass the solar system when needed
- no generator
- batteries are configured as "shared" between both inverters.

@eg4eric

I see that there is brand new firmware out. That firmware doesnt appear to actually address this issue.



   
ReplyQuote
(@clarktheshark)
Eminent Member
Joined: 1 year ago
Posts: 24
Topic starter  

Whatever routine is configured to stop charging if communication is lost is a bit too sensitive IMO! (Why is it losing communication in the first place!!!! Is that the problem?) Also whatever routine is running that takes 10 minutes for it to restart charging seems to be quite long. 



   
ReplyQuote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 2 years ago
Posts: 1287
 

@clarktheshark 
Are you able to have the system online so I can review the settings and some data to find what is causing this issue?

I would still recommend updating the batteries.

0x03= Charge allowed and discharge allowed

0x02= Discharge allowed and no charge allowed



   
ReplyQuote
Page 1 / 2
Share: