(@Anonymous 3251)
Joined: 8 months ago
Posts: 1
Topic starter  

I have an EG4 12000XP off-grid inverter, it's currently equipped with the wifi dongle, but I want to remove that and switch to local monitoring. I'm wanting to try to do that myself versus buying the etherent dongle.

I'm trying to figure out how to get local monitoring via RS485, but I'm running into a port conflict and need help confirming the green terminal block pinout.

My comm board does NOT have the two upper RJ45 ports (CT1/CT2) that most guides reference for RS 485. My board only has BAT COM and Parallel.
My batteries are currently connected to the inverter via the BAT COM RJ45 port for closed-loop comms, so that port is occupied.

<div class="bbImageWrapper js-lbImage" title="1775951026041.png" data-src=" removed link " data-type="image" data-lb-sidebar-href="" data-lb-caption-extra-html="" data-single-image="1" data-fancybox="lb-post-1793427" data-caption="<h4>1775951026041.png</h4><p><a href="https:&#x2F;&#x2F;diysolarforum.com&#x2F;threads&#x2F;eg4-12000xp-rs485-terminals.123716&#x2F;#post-1793427" class="js-lightboxCloser">yam404 · Apr 11, 2026 at 4:44 PM</a></p>"> 

image

What I do have is the green terminal block above.

My questions:
1. Are COM1 and COM2 on the green terminal block the RS485 A+ and B− lines?
2. If so, which is A+ and which is B−?
3. Is there any conflict with the batteries already using BAT COM, or are these completely separate?

Goal is to connect a USB RS485 adapter to the terminal block and read inverter data locally via Modbus.



   
Quote
fkitzmann
(@fkitzmann)
Trusted Member
Joined: 2 years ago
Posts: 78
 

My 2 cents. I don't know if the 12000XP supports monitoring through RS485. I do have a 18KPV and it does have a terminal block that has RS485 on it -

image

See connections g. Note that connections (CT1/CT2) that you talk about are typically reserved for external current transformers. Also in your case COM1 and COM2 are relay connections to start a generator and not RS485. I'm thinking that in the case of the 12000XP. The only RS485 is through the battery connection and the WiFi dongle. I believe in my case, the RS485 is shared with the WiFi dongle connection where as the battery connection is separate (but I would need to measure it. You may be able to use the WiFi connection and make either a break out cable with a HDMI connector on it or you could follow that connection back to the board that it connects to internally. In my case, I'm connecting the RS485 to a RS485 to Ethernet adapter like this -

image

I then set it up for Modbus communications and use Home assistant EG4 inverter Modbus for communications.

I'm not sure what is communicated through the 12000XP dongles RS485 port but you could try it.

I did look some more and see the following - 

  • Port Location: Most users connect to the RJ45 port (often labeled for the Wi-Fi dongle or CT1/CT2) inside the inverter's wiring compartment.
  • Pin Configuration: For custom cables, the standard pinout for RS485 communication on this unit is typically Pin 7 (RS485B) and Pin 8 (RS485A).

With a DVM, my RS485 signals measure +2.5V to ground. Of course this has the digital signal on it. The dongles cable inside my unit has 4 wires, of which the black and white wires appear to have the RS485 signals on them. Have not confirmed which is A or B on dongle cable. You could start by measuring the CT1/CT2 terminals and see if they are close to +2.5V. If you have a scope, you could also look for activity on the terminals.



   
ReplyQuote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 2 years ago
Posts: 1306
 

Can you please share a picture of the inverter?

Those 2 ports are not usable, since the inverter does not use CT's.



   
ReplyQuote
(@pgaffney)
Active Member
Joined: 1 year ago
Posts: 8
 

I just finished setting up a Waveshare RS485-ETHERNET adapter and have successfully got it working with the EG4 12000XP.  Two wires - pins 7 and 8 on the left most RJ45 port (The ones with the plugs in them - just pull out the left most one and plug in a cable that you can make up) and attach to the RS485 A and B pins on the Waveshare.   I set this up so that I can monitor via Home Assistant using the HAC's EG4 Web monitor, which can be set to use  web only, web and RS485, RS485, or local web (no cloud) only.   Can't say if a firmware update on the inverter or batteries is going to cause this all to stop working as it is not a supported configuration - but it is working for now. I will monitor for a few days and let you know if I have any issues.



   
ReplyQuote
(@pgaffney)
Active Member
Joined: 1 year ago
Posts: 8
 

Replying to my own post with an update.  Yes...you can have a dongle (wifi, ethernet) , RS485....just not at the same time.  If you use RS485 the dongle stops working and you get no reporting or control via that interface.  Can't have it all...

 



   
ReplyQuote
(@pgaffney)
Active Member
Joined: 1 year ago
Posts: 8
 

One more comment.   Remove the Wifi or Ethernet dongle if you have it configured to connect via the web.   If you restart the inverter the dongle becomes active and will start sending waaaaaay to many requests - resulting in getting banned for 24 hours.  (sorry about that...)  Remove RS485 connection f you want to use web reporting.



   