I'm looking for a best practices document or guidance re using the Gen port for Smart Load.  I'm considering using it for a sub panel in my garage for EV Charging (40A max).  Thank you in advance for any advice on this topic.


8 Replies
EG4 Eric
Posts: 1303
Admin
(@eg4eric)
EG4 Online Support
Joined: 2 years ago

Are you asking for something like this?

image

Reply
2 Replies
BobAndRoslyn
(@bobandroslyn)
Joined: 2 years ago

Estimable Member
Posts: 99

@eg4eric Thanks, Eric.  That is better than I found.  I dont see a breaker in between the lugs and the "Smart Load", but I assume one would be needed?  Also, please confirm the Max Amperage is 90amp.  Finally, see the follow up questions below regarding "Grid Always On" setting.


Reply
EG4 Eric
Admin
(@eg4eric)
Joined: 2 years ago

EG4 Online Support
Posts: 1303

@bobandroslyn 
You can use up to a 90A breaker. However, I’m unable to confirm the electrical wiring requirements or whether an additional breaker is required between the lugs and the Smart Load since I am not a licensed electrician, but I can look for a better wiring diagram.


Reply
BobAndRoslyn
Posts: 99
Topic starter
(@bobandroslyn)
Estimable Member
Joined: 2 years ago

Some additional background based on this forum that I'd like @eg4eric to chime in on.  Have the issues with Smart Load been addressed and is it reliable?

What "Grid Always On" is supposed to do

Correct — it's meant to bypass the SOC/PV gating entirely whenever grid power is present, so the port only goes dark during an actual outage (and even then, only per whatever SOC floor you've set). 

But real-world behavior has been inconsistent

Digging into the EG4 community forum and the DIY Solar Power Forum, this setting has tripped people up more than once. One user reported that the "Grid Always On" setting didn't seem to affect the results at all in their testing. Another, working with a Signature Solar rep directly on configuration, found that when they tested by turning off the grid breaker, their smart port turned off until the grid breaker was turned back on — despite having Grid Always On enabled and settings meant to keep the port active off-grid at a sufficient SOC, and it took back-and-forth with support to sort out. A third user on a similar system reported the opposite headache: despite enabling Grid Always On and setting a narrow time window with high voltage thresholds as extra insurance, their EV still drew from the battery overnight while on-grid in self-consumption mode. Start PV Power Setting is Being Ignored – Inverters – EG4 Community Forum +2

The pattern across these threads is that the interaction between Grid Always On, the SOC/PV thresholds, and self-consumption/AC-charge modes isn't fully predictable, and sometimes needs vendor support intervention to get behaving as documented — which suggests firmware-version-dependent quirks rather than a clean, reliable override.


Reply
1 Reply
EG4 Eric
Admin
(@eg4eric)
Joined: 2 years ago

EG4 Online Support
Posts: 1303

@bobandroslyn 
I will ask if we have come across these threads in the DIY forum. If you have the links that would help a lot. Are you having these same issues?

image

Reply
BobAndRoslyn
Posts: 99
Topic starter
(@bobandroslyn)
Estimable Member
Joined: 2 years ago

@eg4eric Eric, please address the "The "Grid Always On" setting doesn't seem to affect the results."  According to the notes, this setting is supposed to "Enable for continuous power supply on the GEN port when the grid is on.", so if we have grid, the port will be energized regardless of PV state.  Is this not the case?

 

cc @jared @jarrett @signaturesolarsupport


Reply
1 Reply
EG4 Eric
Admin
(@eg4eric)
Joined: 2 years ago

EG4 Online Support
Posts: 1303

@bobandroslyn 
I apologize for the delayed respond. I must have missed this one, but yes, you are correct! It will be energized regardless of the PV state.


Reply
fkitzmann
Posts: 78
(@fkitzmann)
Trusted Member
Joined: 2 years ago

Just a word of note. I have an 18KPV and was using the Gen port for Smart Load also. It was working properly until I installed a GridBoss later, at which point the generator port (programed as a smart port) opened it''s AC connection to the inverter. Note that this is what currently happens when the inverter is connected to a GridBoss. I requested if a new software update could be produced to make this path work again but it never happened. See post -

18KPV AC Couple mode stopped working after adding GridBoss