Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@dtbaker61 I would differ that this is off topic. With direct modbus control to home assistant , it is possible to write automation that would get c...

10 months ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

The 6000xp firmware ccaa-191011 seems to have fixed the bug with open-loop charge control for LFP... mostly. The resulting charge curve is "correct" m...

10 months ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@ouijifour your reply is completely off-topic for this thread. The issue is faulty charge control by the 12000xp when running "open loop" with user de...

10 months ago
Forum
Topic
Forum
Replies: 3
Views: 1009
Reply
RE: Flexboss 21

Please describe how you want your system to function. Peak Shave is probably not what you are wishing for, all this does it keep your electrical usag...

10 months ago
Forum
Reply
RE: Field Impact Notice- 48V Batteries

@yooperjay Thank you for testing out that you can update the firmware with old versions (and supplying the files). I had a feeling that was possible b...

10 months ago
Reply
RE: Generator integration for off-grid system

@yooperjay yes I just was told that by the EG4 tech-support who finally after a week called me back. it seems like that needs to be made more clear ...

10 months ago
Forum
Reply
RE: Generator integration for off-grid system

@minotto You said your generator is connected to the main inverter. I believe the generator needs to be connected to each inverter when the inverte...

10 months ago
Forum
Topic
Forum
Replies: 3
Views: 1461
Reply
RE: Field Impact Notice- 48V Batteries

Ok, stuff like this drives me crazy. Drove the 2 hours to the cabin...loaded the oldest versions of the firmware both RS232/RS485 that I could find f...

10 months ago
Reply
RE: Updates

Back in October we updated to the 2525 Firmware on the Inverter. Over the next weeks we found MANY anomalies that EG4 could never explain. With the ...

10 months ago
Forum
Topic
10 months ago
Forum
Replies: 1
Views: 1337
Reply
RE: Field Impact Notice- 48V Batteries

Well, I am not the only one! I have 2 batteries but only 1 showing up with the same weird characters for the battery. The configuration shows 2 batt...

10 months ago
Reply
RE: Field Impact Notice- 48V Batteries

@solargear I also experienced the same issue when completing an upgrade yesterday evening on 3x Indoor Wall Mount 280Ah, and I was planning to contact...

10 months ago