EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts - SOLVED!

Good News,   It seems that the Wall Mont battery BMS comms issues causing inverter stop 'seeing there is battery" when set up in Lithium type...

8 months ago
Forum
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts

A positive update, Today I decided to look again at my setup and search for any more error logs in addition to what I have already reported. I...

8 months ago
Forum
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts

I was told yesterday to do cold restart of entire system including BMS, which I did and ... No change. The comms from Wall mount battery BMS to inve...

8 months ago
Forum
Reply
RE: outage blips Flexboss21 + gridboss21

Indeed ppl have issues with indoor Wall Mount batteries comms. See the latest results of trying to fix it: It looks as systematic BMS comms iss...

8 months ago
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts

@eg4eric I have just updated the BMS firmware to the latest. Connected the BMS tools and checked all - see below: YET, When a...

8 months ago
Forum
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts

@eg4eric Have received the cables and took a chance to update Wallmount battery BMS to latest firmware. All went well with update - che...

8 months ago
Forum
Reply
RE: Uninstalling Mini-Split for Warranty

Well, I managed to diagnose the issue with EG4 remotely - the main control board was found faulty. Had it replaced twice and eventually RMA entire o...

9 months ago
Reply
RE: Uninstalling Mini-Split for Warranty

I had my mini split RMA replaced (outdoor unit only) . I had the same concern with pre-charged line set. Therefore I talked with the vendor and made t...

9 months ago
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts

@pawnee the following thread relates to run the battery in Open Loop (Lead Acid) mode. My charge setting are set up accordingly - Its not idea...

10 months ago
Forum
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts

@eg4eric Thank you for the response. Looking forward to receive RS232/usb kit to update the BMS firmware. Brgds K

10 months ago
Forum
Reply
Reply
RE: EG4 14.3kWh indoor wall mount battery BMS comms issues - resulting in blackouts, power blips, and charging restarts - Is BMS firmware update needed?

@EG4 Eric Above is the snapshot of Event Log from my replaced 6000p indicating when the Wall Mount Battery BMS problems started. As mentioned befo...

10 months ago
Forum
Reply
RE: Warning 27, 6000xp with 289AH wall mount battery

@ronster I was told by SS tech that Lead Acid Battery mode is an open loop communication mode (manual mode) and aside some lost functionality (lack...

10 months ago
Forum
Reply
RE: HELP : 12Kpv monitor shows 132V but 0w = not charging batteries from PV

With the battery at 99-100% SoC there is no place to power to go, so PV array does not produce power. Turn some loads on and you will see the PV pro...

10 months ago