GridBOSS and Generac whole-house generator

13 Posts
6 Users
0 Reactions
6,418 Views
Posts: 4
(@wicksmith1)
New Member
Joined: 1 year ago

I was just informed by Signature Solar that the RSD relay port 2 cannot produce 12vdc to keep the battery at the starting battery for the generator charged. If you all find out something different, please let me know.


Reply
1 Reply
(@buff30)
Joined: 1 year ago

New Member
Posts: 3

@wicksmith1 What do you have T1 and N connect to?


Reply
Posts: 19
 eg4c
Topic starter
(@eg4c)
Eminent Member
Joined: 1 year ago

@wicksmith1 I was able to get the generator working after all. You can see this thread for details

 

 


Reply
1 Reply
(@jrkd2015)
Joined: 1 year ago

New Member
Posts: 1

@eg4c Could you please let me know exactly how you have the generator wired to your grid boss?  Is it possible to get some pictures?  I was told that I still needed the ATS for the generac. Any help would be appreciated.


Reply
Posts: 19
 eg4c
Topic starter
(@eg4c)
Eminent Member
Joined: 1 year ago

- Generator wires (thick ones) go into "generator"

image

 

- IMPORTANT IF YOU WANT TO FOREGO ATC: Generator must be reconfigured for "2-wire start"

- inside generac panel: "VAC Load Supply" wire connects to one of the electric phases in the panel. two yellow wires no longer used. All wires from "DC Common", "+12V", "TRANSFER" are no longer used.

20241216 085200

- connect two wires to your generator "2 wire start" PINs, as described here: https://diysolarforum.com/threads/replacing-generac-ats-with-grid-boss.94155/post-1290777 . These could be different on different models. If generator is reprogrammed for 2-wire start, shorting them should start generator, and un-shorting them should stop it


Reply
Posts: 1
(@terry377)
New Member
Joined: 3 weeks ago

I was just digging through some old wiring diagrams for a similar project and saw this. The N1 and N2 wires are meant for utility sensing, but the GridBoss doesn't provide that 240V signal directly, so you’ll need to bypass those using a 2-wire start kit.

I had the same T1 charging issue and worked with Wolf River Electric to pull a separate 120V circuit just for the internal battery maintainer. Running that charging line independently of the inverter outputs ensures the battery stays topped off even when the system is in standby.


Reply