I also have the problem that the Bulk/Float setting doesnt work. Is there a new firmware for this now? Jacob
Hello, I've got my XP6000 running my barn on backup power (EPS) with the battery (soon to be "batteries") being charged via solar. Operating well but...
Perhaps this is a "huge security issue", but for a normal house that does not have these systems at all, with the main service disconnect for the hous...
@ray You may have the same problem i having but I am on lead The system is reading the battery volt right but i have a 2nd battery disconnect if i tur...
The question is why doesn't the Inverter use the battery when set to Time+SOC/Volt but it will use it when set to SOC/Volt. Setting to Time+SOC/Volt p...
@potrero - I'm in exactly the same boat (GB, FB21, 2x outdoor batts) and see the same behavior. I see no good reason WHY the RSD to the inverter shou...
So I have narrowed this down to a logic problem in the inverter related to working modes. One with the AC Charge mode time window and the other when t...
ok, getting back to the original concern.... As far as I can tell, there is NO WAY to obtain a "proper" open loop charge curve, (charge controlled b...
The Remote_Set_Error appears each time the Weather Optimize feature tries to start a charge cycle. I have attached a composite of screen captures sho...