@nathanfaught We are actively working on this and will have an update soon to resolve the issue.
Were you able to get the firmware update installed?If you have the inverter online, I can update the firmware for you.
Do you have setting #3 set to GNE? Sometimes this does require a firmware update depending on what firmware the inverter is on.
The advanced menu has the option to enable Zero export and disable Grid sell back. The only way to make sure that absolutely nothing feeds back to gri...
Not sure what happened exactly, but once you set the Discharge cut off the inverter should stop discharging the batteries. It could be that one of the...
Please send me a PM with your inverter's serial number, I would like to look further into this for you.
Where are the CT's located?I would recommend making sure they are connected and placed properly. It could be using the grid but there could be somethi...
Since the 6000XP is an Off-Grid inverter, it will prioritize solar and battery before using the grid. It will use solar to power the loads and to char...
Which inverters are you using?
Are you seeing any lights on or blinking on the dongle?
Here is a diagram on how to connect the batteries to each other and to the inverter. Also, having the inverter on Lithium brand "1" is the best protoc...
@quailfarmer If there is proper communication between the inverter and batteries it should show the AH. Have you tried clicking up and down on the arr...