RE: How do I get my 6000xp to recognize my eco worthy server rack battery

@charlie Do those batteries support any of the protocols listed in the image?

4 months ago
Forum
Reply
RE: Flexboss in offgrid setting with generator

As Joel mentioned, you would need the GridBoss in order to use a generator, as the FlexBoss was designed to work alongside the GridBoss. The FlexBoss ...

4 months ago
Reply
RE: 12kxp firmware fails to update

Could you please provide your station name or inverter serial number so we can review your system?

4 months ago
Forum
Reply
RE: Control Over RS485?

Are you referring to the Modbus communication protocol for the 12000XP?

4 months ago
Forum
Reply
RE: Smart port status and display differences

@michaelahess As shown on the picture I posted. It does show that your system in already in parallel. This is the reason why the button is not showing...

4 months ago
Reply
RE: Error code 25, 27 on XP6000

@ravasunpower I apologize for the delayed response, I did not see that you replied to this thread. I did see on the DIY forum that you installed anoth...

4 months ago
Forum
Reply
RE: 12000xp and warning 28

@we2 Yes, we do. If the batteries are not on this list, there may still be a chance for communication if they use one of the supported protocols. Howe...

4 months ago
Forum
Reply
RE: firmware for all weather

This is the changelog below ⬇️ You don't have to update it, but you can, so the batteries are up to date.

4 months ago
Reply
RE: XP 6000 keeps shutting down…

I apologize for the delayed response. Were you able to confirm with a voltmeter or multimeter the voltage of the batteries when the warning was showin...

4 months ago
Reply
4 months ago
Forum
Reply
RE: How do I get my 6000xp to recognize my eco worthy server rack battery

Are you trying to have closed loop communication or just open loop (charge/discharge by voltage)?If you have it connected, the inverter should be dete...

4 months ago
Forum
Reply
RE: Integrating LG EM048126P3S7 Series Lithium Ion Batteries

@fsissonApologies for the delayed response. I hadn’t seen your other posts. Please know that we do our best to respond to every post as quickly as pos...

4 months ago
Forum
Reply
RE: Smart port status and display differences

It looks like it's already in parallel. So we need to figure out why it's not showing the correct information. Were you able to change the DIP sw...

4 months ago
Reply
RE: 12000xp and warning 28

You can change the Discharge Current Limit to 250A. This will allow the inverter to discharge 12kW from the battery.

4 months ago
Forum
Reply
RE: Smart port status and display differences

You can go to the Overview tab on the website, where you should see a button that says parallel. If you don’t see this option, just let me know and ...

4 months ago