RE: 48v LL Battery cluster overloading charge amps modbus register

@somej Our battery technicians created a folder for you that includes the firmware for both the 4-DIP and 6-DIP switch batteries. For the 6-DIP switch...

7 months ago
Forum
Topic
Replies: 39
Views: 4374
Reply
RE: 18kPV with Generac 15kw EcoGen

@eagleridge I'm glad you figured it out! I will definitely pass the feedback along to our documentation team. Thank you!

7 months ago
Forum
Reply
RE: EPS overload

@frugal-farmer Here is the link to the Spec sheet for this inverter.EG4-6000XP-Inverter-Spec-Sheet.pdf

7 months ago
Forum
Reply
RE: Confusing BMS Data Displayed on EG4 18kpv Inverters

Are you sharing all 12 batteries with both inverters? Or does each inverter have its own battery bank?

7 months ago
Forum
Reply
RE: Battery 48v 16kwh charging at 9a

Which battery are you using?Does your battery have Luxpower Protocol?

7 months ago
Reply
RE: Batteries disappeared overnight?

@ray Where did you see or hear about the Self-Balancing via BMS? I just want to make sure we clarify any confusion.

7 months ago
Reply
RE: Sudden drop from 23% to 0% SOC

@michaelahess Once you change the inverter to Lead acid, the SOC parameters will not matter since it's going based off of voltage. So, you will need t...

7 months ago
Forum
Reply
RE: 120v generator hooked to a gridboss

@ianscott That is the best solution!

7 months ago
Forum
Reply
RE: Sudden drop from 23% to 0% SOC

To recalibrate the battery, you’ll need to charge it to 57V using either a 48V charger or the inverter set to Lead Acid mode.Are you regularly chargin...

7 months ago
Forum
Reply
RE: Time controls for Generator Charge

Yes, the 2 wore Start/Stop will work when Micro-Grid is enabled.

7 months ago
Forum
Reply
RE: EG4-6000XP – MPPT1 ghost voltage + both MPPTs get stuck after clouds

Are you able to share your station name or inverter's serial number so I can look into this for you?Prior to getting the E017, did you have any issues...

7 months ago
Forum
Reply
RE: 18kPV with Generac 15kw EcoGen

What settings do you have configured for the Generator Charge?

7 months ago
Forum
Reply
RE: Quick help for a newbie - Generator setup not charging the battery

The Chargeverter will definitely help with the charging and cleaning up the dirty power. Thank you for updating us!

7 months ago
Forum