RE: Max 18KPV combined output

As previously mentioned, the 18kPV has a maximum AC output capacity of 12,000W. This limit is fixed and cannot be adjusted through settings.

1 year ago
Forum
Reply
RE: Gridboss backup battery transition to generator?

Yes, if grid goes down, your system will use battery power for loads and once they hit that percentage or voltage that is set, the generator will take...

1 year ago
Reply
RE: EG4 LL4 24V batteries - coms question

I don't know for sure, but if I were to guess, I would say something like Start:23.5V-24V Stop:28V (if you want full batteries, if not, you can set it...

1 year ago
Forum
Reply
RE: How do the different working modes function with a generator

Are you selling back to grid with AC couple?

1 year ago
Forum
Reply
RE: outage blips Flexboss21 + gridboss21

Thank you for sharing this information and keep us updated. I’ll continue looking into the issue and will let you know what I find.

1 year ago
Reply
RE: 6000XP connect with bluetooth

Can you share a screenshot of the message you are getting?

1 year ago
Forum
Reply
RE: Discharge Settings - 6000XP & 3000EHV

The 6000XP does not have a specific setting to force battery discharge. An option is to increase the load demand. Since this is an off-grid inverter, ...

1 year ago
Reply
RE: EG4 LifePower4 V1 Automatic Updater Dongle

I apologize for the confusion. The automatic updater is limited to firmware version V3.37 and cannot be updated or used with any other firmware.

1 year ago
Forum
Reply
RE: outage blips Flexboss21 + gridboss21

I recommend checking all your wires and make sure they aren't loose. Do you have a wiring diagram for your system? If so, can you share it so we can l...

1 year ago
Reply
RE: EG4 LL4 24V batteries - coms question

I found the Bulk/Absorption, Float, and Low DC Cut-Off in the image below. However, regarding communication, if you're unable to set the system to one...

1 year ago
Forum
Reply
RE: 6000xp in UPS mode without cycling battery

When you set AC Charge, set it based off SOC, so this way the inverter will charge batteries with grid when the batteries go under a certain battery p...

1 year ago
Forum
Reply
RE: Start Quick Charge - not operating with Weekly Schedule?

Thank you for bringing this to our attention. We will be looking into this to determine if there's a conflict between the quick charge function and th...

1 year ago
Forum
Reply
RE: Inverter Battery Setting setup- 6000xp

The 6000XP is an off-grid inverter, designed to operate primarily using solar and battery. It will automatically utilize available solar power to char...

1 year ago
Reply
RE: NOBODY ANSWERS THE PHONE

Good afternoon,Thank you for your patience. Due to a high volume of incoming calls, we are not able to answer every call immediately; however, we are ...

1 year ago
Forum
Reply
RE: 3 6000XPs in parallel fans do not run at low wattage

Those temperatures are normal for the inverters. A high temperature warning will appear at 87°C, and a fault will trigger at 92°C. Since you're well b...

1 year ago