Good morning, If the Grid does not have a neutral, I would not connect grid until you have a better answer for this situation. If any damage happens t...
It be recommended to connect each battery to the inverter as shown in the image below but also connecting the batteries together in parallel.
@nothing2crazyThe inverter's cooling fans will automatically activate when the output load exceeds 6kW, or the internal temperature exceeds 75°C.
When the inverter reaches an internal temperature of 83°C, you will begin to get warning and alarms for high temperature.
@krzysiek_kta On these older units, the Dry mode is the same as Dehumidifying mode.
@krzysiek_kta I'm getting with our HVAC Technician about this.
@krzysiek_kta You can use Dry Mode. It will keep the unit in the cooling operation and also help to dehumidify.The unit is variable capacity, so the...
@krzysiek_kta Can you remind me if your batteries currently up to date with the latest firmware?There hasn't been any new ones released at the moment ...
@fkitzmann If you can send the correct one, I can try again and see if that makes a difference. If not, we can have someone reach out to you and possi...
I apologize for the delay on this thread. You are correct. You can use the EG4 BMS app with the antenna. Thank you for sharing!
@cmart1220 I apologize I missed this! If you share your inverter or Gridboss serial number with me, I can look at the alarms and data to identify what...
@adamsonaire I don't believe this is currently possible, based on my understanding, but I'll double-check to confirm. There is a debug mode I can enab...
@walkerThe only way to ensure zero power is exported to the grid is to enable Off-Grid Mode. Keep in mind that when Off-Grid Mode is enabled, the inve...
@rpeatfield I will send you a DM.
@fkitzmann I went ahead and changed one of the settings in your system. I changed the LCD Type to "LCD Screen Kit". Please let me know if this resolve...